    Fire alarm vfd shutdown

    I’m using a addressable fire alarm relay to shut down a vfd. Is the best way to achieve this by running the enable circuit thru the dry contacts on the relay?

  2. #2
    Join Date
    Jun 2003
    Location
    NE (9.06 miles @5.9 Degrees from Winged Horses)
    Posts
    11,260
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    There may be better ways, but that is what I use when I want it to stop via a master control relay.
    Tom
    TBLO

  3. #3
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    8,742
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    That’s probably the best way because by using the enable circuit, you override any ramp down or braking settings and immediately kill power to the motor, which is what you often want in an emergency, especially on a pump or fan.

    If the machine is of a type that can benefit from braking being done via the VFD however, like a conveyor or a centrifuge, keep that in mind because that may dictate using a regular Stop command.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  4. #4
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,645
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Jraef View Post
    That’s probably the best way because by using the enable circuit, you override any ramp down or braking settings and immediately kill power to the motor, which is what you often want in an emergency, especially on a pump or fan.

    If the machine is of a type that can benefit from braking being done via the VFD however, like a conveyor or a centrifuge, keep that in mind because that may dictate using a regular Stop command.
    If killing the power to a machine or device rather than using a shutdown procedure would cause a greater risk to the public, then you are allowed to send the signal to a controller. Think elevator recall. The same would go for an escalator or moving walkway.

  5. #5
    Join Date
    Jul 2008
    Location
    Minnesota
    Posts
    589
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks guys