Thread: proper use of bonding wire in LFMC? just grounded locknuts?

  1. #11
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,578
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by emiller233 View Post
    i did, i can deal with the 6' max length. can add a chunk of RMC if needed to shorten the LFMC length
    FYI, that 6 foot length is only limitation on using the flex as the EGC, if you pull a EGC inside there is no length restriction.
    I live for today, I'm just a day behind.

  2. #12
    Join Date
    Dec 2016
    Location
    pittsburgh, pa
    Posts
    110
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    i realized that after i read thru it a 2nd time. customer just told me last night the want RMC as close to the device as possible now...

    for fittings, we can just use the normal fittings such as TNB 5231