    Lighting pole grounding in concrete medians

    Hi all, my apologizes if this question has been asked.

    I'm doing some work in Ontario where new metal lighting poles on concrete bases are being mounted in a concrete median.
    I cannot seem to find any related documents stating every lighting pole needs a ground rod placed next to it, but I have read over and over that every pole needs a ground rod (lightning protection maybe?). If they are in fact required, how would they be mounted in the concrete? Do I install a handwell adjacent to the pole to allow for connections and testing?

    Any help would be greatly appreciated.

    Regards,

  2. #2
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,880
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    I moved this to the Canadian forum. In the US there is no need for a ground rod at every pole. It is often done but it is not required. Hopefully some Canadians will reach out. @electricguy @Eddy_Current @daveEM
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  3. #3
    Join Date
    Nov 2015
    Location
    Canada
    Posts
    22
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by EastCanadian View Post
    Hi all, my apologizes if this question has been asked.

    I'm doing some work in Ontario where new metal lighting poles on concrete bases are being mounted in a concrete median.
    I cannot seem to find any related documents stating every lighting pole needs a ground rod placed next to it, but I have read over and over that every pole needs a ground rod (lightning protection maybe?). If they are in fact required, how would they be mounted in the concrete? Do I install a handwell adjacent to the pole to allow for connections and testing?

    Any help would be greatly appreciated.

    Regards,
    Lightning protection is not required for each pole.
    Every pole needs to be bonded back to the source, with proper grounding at the source.
    ESA has a streetlighting guide online. https://www.esasafe.com/assets/files...r2-May2015.pdf
    If you happen to get the work, they also have a guide for Traffic pole/controller bonding as well.

    If you did require a ground rod at any pole, I would just bond to rebar in the concrete base.

  4. #4
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,749
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by 414Mhz View Post
    If you did require a ground rod at any pole, I would just bond to rebar in the concrete base.
    Wouldn't you want the circuit EGC to be part of that connection?
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  5. #5
    Join Date
    Nov 2015
    Location
    Canada
    Posts
    22
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    Wouldn't you want the circuit EGC to be part of that connection?
    We don't have EGC's here

    But yes, any supplemental ground rods installed beyond the source, you would bond to the ground wire.

  6. #6
    Join Date
    Jun 2019
    Location
    Halifax, Nova Scotia, Canada
    Posts
    2
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by 414Mhz View Post
    We don't have EGC's here

    But yes, any supplemental ground rods installed beyond the source, you would bond to the ground wire.
    Perfect!
    Thank you so much for the help team!!