Thread: Gas range load calculation

  1. #1
    Join Date
    Apr 2017
    Location
    USA
    Posts
    294
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)

    Gas range load calculation

    Hello,

    Is there anywhere in NEC where you are require to put a certain load(kW) in load calculations for a range even though its gas?

  2. #2
    Join Date
    Feb 2003
    Location
    Connecticut
    Posts
    3,591
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by shortcircuit1 View Post
    Hello,

    Is there anywhere in NEC where you are require to put a certain load(kW) in load calculations for a range even though its gas?
    220.84

  3. #3
    Join Date
    Feb 2008
    Location
    Texas
    Posts
    1,082
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    220.55 (2017) Speaks to ELECTRIC cooking appliances. I've never included a gas range in my calculations.

  4. #4
    Join Date
    Apr 2017
    Location
    USA
    Posts
    294
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by david luchini View Post
    220.84
    There's nothing in 220.84 for gas ranges.

  5. #5
    Join Date
    Feb 2003
    Location
    Connecticut
    Posts
    3,591
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by shortcircuit1 View Post
    There's nothing in 220.84 for gas ranges.
    Yes there is. Read the exception.

  6. #6
    Join Date
    Apr 2017
    Location
    USA
    Posts
    294
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by david luchini View Post
    Yes there is. Read the exception.
    The exception says you take the lowest between electric cooking and without electric cooking. I am clear on service size. Is there anywhere in NEC where it specifically says you need to add a certain kW for gas ranges(Perhaps in the future owner may switch to electric). I wasn't able to find it.

  7. #7
    Join Date
    Apr 2017
    Location
    USA
    Posts
    294
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Chamuit View Post
    220.55 (2017) Speaks to ELECTRIC cooking appliances. I've never included a gas range in my calculations.
    Thats exactly what i have but just want to see if anyone has other code references in NEC.

  8. #8
    Join Date
    Feb 2003
    Location
    Connecticut
    Posts
    3,591
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by shortcircuit1 View Post
    The exception says you take the lowest between electric cooking and without electric cooking. I am clear on service size. Is there anywhere in NEC where it specifically says you need to add a certain kW for gas ranges(Perhaps in the future owner may switch to electric). I wasn't able to find it.
    220.84 says to add 8kw for each gas range to use the optional method.

  9. #9
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,683
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by david luchini View Post
    220.84 says to add 8kw for each gas range to use the optional method.
    Have we established that this is a multi-family dwelling, since that's what 220.84 is all about?

  10. #10
    Join Date
    Feb 2003
    Location
    Connecticut
    Posts
    3,591
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by gadfly56 View Post
    Have we established that this is a multi-family dwelling, since that's what 220.84 is all about?
    No, but that wasn't the question. The question was is there anywhere in the NEC that requires you to put a certain kw for gas ranges into load calcs.

    The answer is 220.84. It requires you to put in 8kw for gas ranges in it's load calc.