    PNL BUS/BRKR RATING
    In what situation would a panelboard have different amperage for the MCB and the bus? Most times I see them the same but do remember them being different once in while? Thanks.
  2. #2
    Join Date
    Dec 2011
    Wisconsin
    Posts
    681
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mstrlucky74 View Post
    Some panels have a 200 amp MCB with 225 amp bus. I believe in some cases it is cheaper for a manufacturer to make one bus and use it in multiple panelboards.
  3. #3
    Join Date
    Jul 2006
    Posts
    8,861
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by packersparky View Post
    Actually in all cases. Panel bus sizes are only going to be among a few ratings, different from one mfr to another. 60A, then 100 or 125A, 200/225/ 250A, 400A, 600A, 1200A etc. So if you need a 90A main breaker your panel bus is going to be 100A or 125A, depending on the standard product your selected mfr uses. If you need a 300A main, its going to be a 400A bus, etc.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...
  4. #4
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    5,943
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    This comes up in solar a lot. I agree manufacturers use the same bus for different main breakers, but the manufacturer rarely will tell you or document this.
    I had some 125 and 250A Siemens factory MLO panelboards and they were exactly the same. I took one of each out of the box and was looking over them and I mixed them up and couldn't tell which was the "125" and which was the "250"
    Edit. Just wanted to be clear that you can factory order whatever you want