    Handhole for Service Conductors

    I have a couple of questions for service conductors between an exterior utility pad-mounted transformer and a Main Switchboard.

    1. Can there be a in-ground handhole/pullbox for the service conductors? I am assuming there is nothing in the NEC which disallows this.
    2. Can these service conductors be spliced in the in-ground handhole/pullbox?


    I appreciate the help in advance.

    Thanks.

  2. #2
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,943
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Shujinko View Post
    I have a couple of questions for service conductors between an exterior utility pad-mounted transformer and a Main Switchboard.

    1. Can there be a in-ground handhole/pullbox for the service conductors? I am assuming there is nothing in the NEC which disallows this.
    2. Can these service conductors be spliced in the in-ground handhole/pullbox?


    I appreciate the help in advance.

    Thanks.
    Sure and Sure - although might want to check with the POCO if these are unmetered conductors. Often such a setup is where the service point is, but it could be completely customer owned with the service point at the tranny spades too.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  3. #3
    Join Date
    Dec 2006
    Location
    Eastern Oregon
    Posts
    3,820
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Like mentioned above, from an NEC standpoint, there are no issues.

    The utility co. may want to put their two cents in, so it's worth a call in case they have any thoughts on the subject.

  4. #4
    Join Date
    Aug 2010
    Posts
    204
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks. I talked to the POCO and they are ok with the handhole and splice.