    Is the neutral in 240v circuit a CCC?

    In dryer and range circuits, is the neutral considered a current carrying conductor for derating purposes?

  2. #2
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,904
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Coppersmith View Post
    In dryer and range circuits, is the neutral considered a current carrying conductor for derating purposes?
    Nope! Free lunch!
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  3. #3
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    20,349
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    IMHO, either the neutral is unused and does not carry current or it is part of an MWBC and is not counted. However an MWBC may not be strictly allowed to carry 240V line to line loads. The principle that any increase in neutral current must correspond to reduced current in one of the hots would still apply.

    Sent from my XT1585 using Tapatalk

  4. #4
    Join Date
    Aug 2008
    Posts
    268
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Does your dryer have a 110 volts load?

  5. #5
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,503
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    If it's from a 1Ø, 240 volt system then the neutral does not count as a CCC. If it's from a 3Ø, 208Y/120 volt system then it does count. Since you said 240 volts you're good.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  6. #6
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,578
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    If it's from a 1Ø, 240 volt system then the neutral does not count as a CCC. If it's from a 3Ø, 208Y/120 volt system then it does count. Since you said 240 volts you're good.
    I agree, same appliance generally can be used on either system and neutral will be a CCC if supplied from a wye system.
    I live for today, I'm just a day behind.

  7. #7
    Join Date
    Jun 2016
    Location
    Kitsap, WA
    Posts
    9
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by bobby ocampo View Post
    Does your dryer have a 110 volts load?
    If this is in the US of A, most dryers do. The motor, and computer is a 120vac load. The only load internal of the machine that is 240vac is the heater itself, which is typically around 5400 watts depending on brand. Some machines imported from overseas, such as Bosch or a lot of the 24 inch Apartment units, only use 240vac.

  8. #8
    Join Date
    Jan 2008
    Posts
    9,784
    Mentioned
    0 Post(s)
    Tagged
    1 Thread(s)
    Seems to me if the dryer needs a neutral connected, then the neutral is a CCC. If the dryer does not have a neutral terminal, then the neutral remains unconnected and is not a CCC.
    BB+/BB=?

  9. #9
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,723
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mivey View Post
    Seems to me if the dryer needs a neutral connected, then the neutral is a CCC. If the dryer does not have a neutral terminal, then the neutral remains unconnected and is not a CCC.
    Doesn't matter. As GoldDigger said above, any neutral current is current not being carried by a line conductor, so the neutral still need not be counted on 1ph.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  10. #10
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,578
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mivey View Post
    Seems to me if the dryer needs a neutral connected, then the neutral is a CCC. If the dryer does not have a neutral terminal, then the neutral remains unconnected and is not a CCC.
    If dryer needs a neutral connected then yes it does carry current. OP's question AFAIK is whether it needs counted as a CCC when it comes to ampacity adjustment purposes. On a 120/240 singe phase system, it only carries unbalanced current between the ungrounded conductors. In a wye system with only two of the phase conductors as the circuit, it doesn't carry imbalance current and has to be counted as a CCC for ampacity adjustment reasons.
    I live for today, I'm just a day behind.