    Student, have a few questions about breakers/ power in general

    Hello fellow electrical enthusiasts,

    I am currently a student studying electrical engineering, currently pursuing an engineering internship and very interested in the field of power systems, especially in low voltage/ building applications.

    I have a few questions about some concepts within power engineering.

    Let's say we have a 3 phase circuit breaker that is supposed to be delivering power to a building. The power is calculated for each phase (a,b,c) and then the total power is adjusted (using NEC/ other code) based on demand factor, and that allows us to calculate whether or not we're overloading the breaker (for example, some breakers have 225 amp rating).

    Let's say I calculate 20kVA per phase (say we're doing something simple like receptacles/ lights). Does this mean the total power being used by the breaker is 60kVA, or is it 20kVA * sqrt(3), which is 34kVA. Is the 225 amp rating per phase, or is it the total current being absorbed at once by the system?

    Now let's also assume the breaker is connected to a 3 phase motor. This motor draws 14,411 VA per phase. The strange thing is, that the motor is rated at 20 Horsepower, which is equal to 14,411 Watts. But if you add up all the phases (14,411*3), this gives you 58 horsepower.

    Another thing that is confusing me. If we have a panel that isn't connected to anything, let's say it's rated at 225 Amps at 120 volts. Does that mean this panel is using power, even though it's connected to nothing?

    Thank you for any help

  2. #2
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    11,213
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by sengineer101 View Post
    Another thing that is confusing me. If we have a panel that isn't connected to anything, let's say it's rated at 225 Amps at 120 volts. Does that mean this panel is using power, even though it's connected to nothing?
    If no current is flowing then no power is being used. P = VI, and if I = 0, then P = 0. How far along are you in your EE studies? That's first semester circuits stuff.

  3. #3
    Join Date
    Sep 2009
    Posts
    1,314
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Generally if you're calculating breaker and wire size, the unit or dimension you want is Amps. You're talking about knowing if you're overloading the equipment, it's an Amp rating.

    Calculating for the load, it's probably mostly all kW at that point. Determine or calculate the total. Next you may have a choice of system voltage. System voltage might be relatively fixed once the choice has been made, then you can convert to Amps to get equipment sizes.

    I've never used kW per phase. It would be load total kW, then the available or choice of system voltage, 480, 240, 208, then the choice or availability of single or three phase supply connection. Once you know load total kW and system voltage, single or three phase, then you can convert to Amps per phase which your equipment is rated for.
    Last edited by __dan; 06-12-19 at 08:06 PM.
    Lasciate ogne speranza, voi ch'intrate

  4. #4
    Join Date
    Jul 2014
    Location
    Lancaster, PA
    Posts
    243
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by sengineer101 View Post
    Hello fellow electrical enthusiasts,

    I am currently a student studying electrical engineering, currently pursuing an engineering internship and very interested in the field of power systems, especially in low voltage/ building applications.

    I have a few questions about some concepts within power engineering.
    Your thirst for knowledge (along with your enthusiasm) is laudable. This tells me that the electrical field *may* be a good fit for you. Here’s a tip for you, from a 62 year old retired electrical engineer who worked in heavy industry and power his whole career:

    With only a very few exceptions, the best engineers have hands-on experience as grunts, helpers, apprentices, etc. Get yourself in with an electrical contractor or find work in an industrial setting, or wiring houses. Such experience is invaluable. Good luck to you.

  5. #5
    Join Date
    Jan 2011
    Location
    United States
    Posts
    9,362
    Mentioned
    1 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by sengineer101 View Post
    Hello fellow electrical enthusiasts,

    I am currently a student studying electrical engineering, currently pursuing an engineering internship and very interested in the field of power systems, especially in low voltage/ building applications.

    I have a few questions about some concepts within power engineering.

    Let's say we have a 3 phase circuit breaker that is supposed to be delivering power to a building. The power is calculated for each phase (a,b,c) and then the total power is adjusted (using NEC/ other code) based on demand factor, and that allows us to calculate whether or not we're overloading the breaker (for example, some breakers have 225 amp rating).

    Let's say I calculate 20kVA per phase (say we're doing something simple like receptacles/ lights). Does this mean the total power being used by the breaker is 60kVA, or is it 20kVA * sqrt(3), which is 34kVA. Is the 225 amp rating per phase, or is it the total current being absorbed at once by the system?

    Now let's also assume the breaker is connected to a 3 phase motor. This motor draws 14,411 VA per phase. The strange thing is, that the motor is rated at 20 Horsepower, which is equal to 14,411 Watts. But if you add up all the phases (14,411*3), this gives you 58 horsepower.

    Another thing that is confusing me. If we have a panel that isn't connected to anything, let's say it's rated at 225 Amps at 120 volts. Does that mean this panel is using power, even though it's connected to nothing?

    Thank you for any help

    Per phase. So a 225 amp breaker is 225 amps per phase.


    225 amps x 208 volts x 1.73= 81kva.



    If no current is flowing no power or work is being done.


    Technically you will have capacitance from the busbars to ground (panel tub), and because that reactive current is flowing through conductors with resistance, a very minuet amount of power is used/dissipated. But we are talking micro watts and its negligible.

  6. #6
    Join Date
    Jan 2011
    Location
    United States
    Posts
    9,362
    Mentioned
    1 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by Iron_Ben View Post
    Your thirst for knowledge (along with your enthusiasm) is laudable. This tells me that the electrical field *may* be a good fit for you. Here’s a tip for you, from a 62 year old retired electrical engineer who worked in heavy industry and power his whole career:

    With only a very few exceptions, the best engineers have hands-on experience as grunts, helpers, apprentices, etc. Get yourself in with an electrical contractor or find work in an industrial setting, or wiring houses. Such experience is invaluable. Good luck to you.
    Could have done without the first few sentences.

  7. #7
    Join Date
    Feb 2003
    Location
    Wisconsin
    Posts
    10,348
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by sengineer101 View Post
    Now let's also assume the breaker is connected to a 3 phase motor. This motor draws 14,411 VA per phase. The strange thing is, that the motor is rated at 20 Horsepower, which is equal to 14,411 Watts. But if you add up all the phases (14,411*3), this gives you 58 horsepower.
    The conversion between HP and kW will always result in a lower value than what you calculate for the input power.
    Remember motors are rated in output power, you must account for the losses (e.g.. Power Factor and Efficiency) in the conversion of power between electrical and mechanical.
    Just because you can, doesn't mean you should.

  8. #8
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    7,858
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    190614-0815 EDT

    sengineer101:

    I have questions about your education.

    At what school are you attending for your EE program?
    At what level are you in this program?
    Have you previously been an electrician, or studied in some trade area?
    What is an engineering internship? Doing what, and where?

    There are some strange things in your first post. An EE student is likely to have had high school physics, and certainly is required to have college physics before taking EE courses. This should mean that you know power is additive, and in most cases does not involve vector or phasor addition.

    Three phase concepts are not likely taught in physics, or first year EE courses. Early courses are going to cover basics. Where would you have been exposed to an equation with 1.732 in it without a derivation of where that constant came from?

    I think electricians view and think about how circuits work differently than do electrical engineers. Electrical engineers are taught about basic concepts and how to apply these basics to more complex problems. Electricians are taught more along the line of --- here is a rule, follow it.

    How are multipole breakers rated? Each pole has exactly the same rating of each other pole, and that is the rating of the breaker. If two poles carry no current and one pole exceeds its trip time curve does the breaker trip?

    Suppose you have a 3 phase wye source with 120 V line to neutral, and you load line to line with a resistance of value R. What is the current in each line including neutral? What value of R will cause the breaker to trip? You have to make assumptions and fill in the missing information to provide an answer.

    For this same source you have 3 equal resistors connected in delta dissipating 1500 W each. What are the various line currents including neutral?

    Let's say I calculate 20kVA per phase (say we're doing something simple like receptacles/ lights). Does this mean the total power being used by the breaker is 60kVA, or is it 20kVA * sqrt(3), which is 34kVA. Is the 225 amp rating per phase, or is it the total current being absorbed at once by the system?
    So that you can easily visualize the problem consider the source is wye and the loads are line to neutral.

    First, kVA is not necessarily equal to power. But for a resistive load power does equal kVA. So assume resistive. Since power is additive the total power is 60 kW. Where does sqrt(3) come from? Out of the blue sky?

    Now let's also assume the breaker is connected to a 3 phase motor. This motor draws 14,411 VA per phase. The strange thing is, that the motor is rated at 20 Horsepower, which is equal to 14,411 Watts. But if you add up all the phases (14,411*3), this gives you 58 horsepower.
    How many watts per horse power? See https://www.google.com/search?q=hp+t...hrome&ie=UTF-8
    745.7 * 20 = 14,914 or
    746 * 20 = 14,920
    Where did 14,441 come from? 722.05 is the result of 14.441/20.
    But as pointed out by jim dungar that is not the electrical input.

    Breakers trip on current not power.

    Another thing that is confusing me. If we have a panel that isn't connected to anything, let's say it's rated at 225 Amps at 120 volts. Does that mean this panel is using power, even though it's connected to nothing.
    A physics class background would answer this question.

    .




    .

  9. #9
    Join Date
    Jan 2019
    Location
    UK
    Posts
    531
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jim dungar View Post
    The conversion between HP and kW will always result in a lower value than what you calculate for the input power.
    Remember motors are rated in output power, you must account for the losses (e.g.. Power Factor and Efficiency) in the conversion of power between electrical and mechanical.
    Why not just stick with kW?
    Power is power.
    For me, and most of the rest of the world, HP is a redundant unit.

  10. #10
    Join Date
    Jun 2019
    Location
    Houston, Texas, United States
    Posts
    3
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I probably should have paraphrased my question. I know that when no load is connected, we don't draw power. But we still need to account for the load operating at maximum capacity when we do load calculations. For example, a 180 VA plug may be connected to nothing (thus drawing no power), but we still need to add it into our panel schedules when calculating the rating. That's what was confusing me. But I get it now.

    Also, the sqrt(3) is derived from the relationship between VL-L and VL-N in a 3 phase system. No need to insult my education. I've never worked with power systems outside a class setting (analysis, etc) so this is very confusing to me. I've been mostly exposed to single phase circuits so the whole 3 phase systems, delta to wye, induction motors etc is still a learn in progress.
    Last edited by sengineer101; 06-14-19 at 12:51 PM.