    STRENGTH OF PANEL COVER IN RELATION TO ARC BLAST

    What is the strength of Panel board cover, switchboard cover in accordance with Arc Blast? Do you have a table of the Cover Strenght in relation with the thickness of the metal?

  2. #2
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    8,840
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    If the gear in question is not listed as Arc Resistant, it's irrelevant in that the cover is not actually required to remain intact in an arc blast event. There are no standards other than those for Arc Resistant Equipment that address this one way or the other. From an electrical and arc flash safe work practices standpoint in NFPA 70E, you are not actually required to use PPE or other protective measures if the enclosure is closed, even though there is no guarantee that it will not come apart in an arc blast event because the risk of that is considered low.

    If the gear is listed as Arc Resistant, the thickness of the metal is whatever it takes to withstand the forces of the available incident energy it is rated for. Manufacturers attain that with a number of strategies involving forming and bracing, not just metal thickness alone. Certification is attained only by destructive witnessed testing at qualified facilities.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  3. #3
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    2,483
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I'm sure how strong they are, but I will usually shield myself with the panel door when I flip on a breaker.

  4. #4
    Join Date
    Mar 2003
    Location
    Vermont
    Posts
    2,594
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    It's an interesting thought......i guess i'll be more aware of missing screws now ~RJ~

  5. #5
    Join Date
    Aug 2008
    Posts
    268
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If Arch Flash Suit has a rating why will a cover or the thickness of the panel metal sheet have no rating?

  6. #6
    Join Date
    Aug 2008
    Posts
    268
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    What is the cal/cm2 ratings of the metal cover of a panel or switchgear? Any table from panel builders?

  7. #7
    Join Date
    Aug 2008
    Posts
    268
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Jraef View Post
    If the gear in question is not listed as Arc Resistant, it's irrelevant in that the cover is not actually required to remain intact in an arc blast event. There are no standards other than those for Arc Resistant Equipment that address this one way or the other. From an electrical and arc flash safe work practices standpoint in NFPA 70E, you are not actually required to use PPE or other protective measures if the enclosure is closed, even though there is no guarantee that it will not come apart in an arc blast event because the risk of that is considered low.
    How come that some metal covers are thick and others like panel board are thin? How will a panel builder decide what thickness to use in the cover? How do they decide to determine the strenght of the cover?

    Quote Originally Posted by Jraef View Post
    If the gear is listed as Arc Resistant, the thickness of the metal is whatever it takes to withstand the forces of the available incident energy it is rated for. Manufacturers attain that with a number of strategies involving forming and bracing, not just metal thickness alone. Certification is attained only by destructive witnessed testing at qualified facilities.
    What specific UL test standard do they use in the test for panelboards and switchboards?

  8. #8
    Join Date
    Aug 2008
    Posts
    268
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Coppersmith View Post
    I'm sure how strong they are, but I will usually shield myself with the panel door when I flip on a breaker.
    I have seen an ATS that had an Arc Blast and left a whole in front of the cover.

  9. #9
    Join Date
    Aug 2008
    Posts
    268
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by bobby ocampo View Post
    I have seen an ATS that had an Arc Blast and left a hole in front of the cover.
    hole

  10. #10
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    8,840
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by bobby ocampo View Post
    If Arch Flash Suit has a rating why will a cover or the thickness of the panel metal sheet have no rating?
    Different issues. An Arc Flash Suit protects you from being burned. What I mean by "no rating" is that if there is an arc BLAST inside of the equipment, a cover blowing open can become shrapnel and kill you, suit or no suit.

    https://www.youtube.com/watch?time_c...&v=9lbiYAMsOEY