    A concrete floor containing low and 120v wiring conduits have been damaged and are being replaced into an installed box. I thought there was a code req separation of voltages, not in ch3, not in ch1, or ch2. I know it's there. I think it's there?
    Any ideas?
  2. #2
    Join Date
    Feb 2008
    Texas
    Posts
    1,082
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    800.133.A.2 what you are looking for?
  3. #3
    Join Date
    Dec 2015
    Posts
    55
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Chamuit View Post
    Thanks for the chapter 8 stuff.
    No I thought there was req's about separation barriers installed in pannels, boxes. ect. Guess I must have imagined it.
    Thanks
  4. #4
    Join Date
    Nov 2010
    Fort Collins, Colorado
    Posts
    2,948
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Russell Ensslin View Post
    Any ideas?
    It is likely that these can not be in the same box. Is this a class 2 circuit?
  5. #5
    Join Date
    Dec 2015
    Posts
    55
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by texie View Post
    Yes
    What about a barrier?
  6. #6
    Join Date
    Nov 2010
    Posts
    2,948
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yes
    that would work. Barriers are available for 4 square boxes.
  7. #7
    Join Date
    Feb 2008
    Texas
    Posts
    1,082
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    800.133.A.1 ex #1 & #2 then.
  8. #8
    Join Date
    Dec 2015
    Posts
    55
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Hope the topic isn’t dead but I still need code for the separation of low (120)and high voltage208^ in the same box
  9. #9
    Join Date
    Feb 2003
    Fl
    Posts
    17,756
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    There is none, 120, 240, 277, 480, are allowed in the same raceways and enclosures, see 300.3(C). Higher and lower voltages have some particulars that needs to be adhered to.
    There are also concerns if devices are in the same box with multiple voltages.
    Roger
    Join Date
    Feb 2003
    Bremerton, Washington
    Posts
    8,207
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    208 is 120 to ground.
    Please see 300.3(C)(1)
    And the IN at the end, most miss this, and try to use a class 2 circuit with 600 volt insulation in a raceway with power and lighting.