Thread: Inspector crazy or me?

  1. #21
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,644
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    I say that, if the box isn't supporting the fixture, its fixture rating is not relevant. The exception need not apply because the rule doesn't.
    That is my thought, but then more recently they messed with that concept when it comes to paddle fan rated boxes being required in some situations even if a paddle fan isn't going to be installed. Nothing wrong with supporting those separate from the box either - or at least never was before

    Supporting from box may be more convenient but not an absolute must do it that way.
    I live for today, I'm just a day behind.

  2. #22
    Join Date
    Jan 2008
    Posts
    9,784
    Mentioned
    0 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by Coppersmith View Post
    I'm not sure which question you are referring to. The only question I see that is related is "Is this structurally sound enough to mount a vanity sconce on". Since the question was not answered by the manufacturer but instead by a bunch of random people I don't take the answers as authoritative.

    Agree.
    BB+/BB=?

  3. #23
    Join Date
    Jan 2008
    Posts
    9,784
    Mentioned
    0 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by Chamuit View Post
    https://carlonsales.com/techinfo/faqs/FAQ-ZipBoxes.pdf

    Last page - 6lbs. and acceptable for wall mounted fixtures.
    There ya go.
    BB+/BB=?

  4. #24
    Join Date
    Jul 2015
    Location
    Wilmington, NC USA
    Posts
    794
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    At one time didn't the NEC require light fixtures to be supported with 8-32 screws at a minimum?

  5. #25
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,875
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    I assume they are furring out the wall. How far will that be. An octagon box on the block may work If sheetrock is being glued to the block the a pancake box would work
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  6. #26
    Join Date
    Jun 2003
    Location
    NE (9.06 miles @5.9 Degrees from Winged Horses)
    Posts
    11,414
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by oldsparky52 View Post
    At one time didn't the NEC require light fixtures to be supported with 8-32 screws at a minimum?
    I believe so and IDR when they added the 6-32 and 6# rule.

    How many any of us weigh those fixtures?
    Tom
    TBLO

  7. #27
    Join Date
    Apr 2005
    Location
    Atlanta,GA
    Posts
    6,468
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Coppersmith View Post

    Inspector's comment: "the vanity box is not rated for fixtures"
    Quote Originally Posted by growler View Post

    Did he fail the inspection or did he just make a comment ?
    Quote Originally Posted by Coppersmith View Post
    He failed the inspection.
    I agree that I probably wouldn't use a plastic switch box for a sconce vanity light because people tend to buy the biggest gaudiest piece of crap they can find for the vanity ( with three heads ).

    But how does the inspector know that you are not going to use a bar light in which case this would be just as good as any other.

    Many times on new construction there will not be any box mounted for rough-in inspection because the exact center of the vanity is unknown. So there is just a little extra cable left in the wall and then an old works box box and a bar light used.
    The 95% of people that you can't trust give the other 5% a bad name.

  8. #28
    Join Date
    Jan 2008
    Posts
    9,784
    Mentioned
    0 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by growler View Post
    I agree that I probably wouldn't use a plastic switch box for a sconce vanity light because people tend to buy the biggest gaudiest piece of crap they can find for the vanity ( with three heads ).

    But how does the inspector know that you are not going to use a bar light in which case this would be just as good as any other.

    Many times on new construction there will not be any box mounted for rough-in inspection because the exact center of the vanity is unknown. So there is just a little extra cable left in the wall and then an old works box box and a bar light used.
    So true, so true.
    BB+/BB=?

  9. #29
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,644
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    I believe so and IDR when they added the 6-32 and 6# rule.

    How many any of us weigh those fixtures?
    Cheap fixtures from big box stores are not that heavy.

    Many quality fixtures aren't really that heavy these days either - they aren't the quality they were years ago though.
    I live for today, I'm just a day behind.

  10. #30
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    2,488
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Ok. So I have the answer. The fixture to be installed is 4.5 lbs. The new inspection is tomorrow. The GC will be escorting the inspector and I have armed him with the appropriate code section. Now I'm expecting him to say "how do I know they won't put a heavier one on later". I told the GC to remind the inspector he can only base his inspection on what we do, not what we could do.

    Sent from my SM-G950U using Tapatalk