    Inspector crazy or me?

    I installed this box on a block wall to hold a bathroom vanity light. (I cut a hole in the block and tapcon'ed the bracket to the block after flattening it out.)

    https://www.homedepot.com/p/Carlon-1...-40R/202077339

    Inspector's comment: "the vanity box is not rated for fixtures"

    True or not?

  2. #2
    Join Date
    Mar 2003
    Location
    New England
    Posts
    13,959
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Going from memory, the NEC allows a 6 pound rating on 1-gang boxes. So, the inspector is not right as long as you're within that rating.

  3. #3
    Join Date
    Jun 2003
    Location
    NE (9.06 miles @5.9 Degrees from Winged Horses)
    Posts
    11,419
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Coppersmith View Post
    I installed this box on a block wall to hold a bathroom vanity light. (I cut a hole in the block and tapcon'ed the bracket to the block after flattening it out.)

    https://www.homedepot.com/p/Carlon-1...-40R/202077339

    Inspector's comment: "the vanity box is not rated for fixtures"

    True or not?
    The Q&A in your link says not for fixtures. I agree. Most likely would work until you’re well past retirement.
    Tom
    TBLO

  4. #4
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    2,489
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    The Q&A in your link says not for fixtures. I agree. Most likely would work until you’re well past retirement.
    I'm not sure which question you are referring to. The only question I see that is related is "Is this structurally sound enough to mount a vanity sconce on". Since the question was not answered by the manufacturer but instead by a bunch of random people I don't take the answers as authoritative.


  5. #5
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,944
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    What first comes to mind is that fixture boxes have #8 screws not #6, but I am not sure 8's are required for fixtures anywhere. 410.36(A) sends you to 314 but nothings specifically requires #8 screws or a box specifically desinged for a fixture. Maybe dig into the listing/instructions for a single gang box and see if says not for fixtures?
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  6. #6
    Join Date
    Feb 2008
    Location
    San Antonio, Texas
    Posts
    685
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    At one time, wall mount fixtures were allowed to be mounted with 6/32 screws

  7. #7
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,944
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by JDB3 View Post
    At one time, wall mount fixtures were allowed to be mounted with 6/32 screws
    Are they not now?
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  8. #8
    Join Date
    Apr 2007
    Location
    Berkeley, CA
    Posts
    1,906
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by peter d View Post
    Going from memory, the NEC allows a 6 pound rating on 1-gang boxes.
    Indeed, 314.27(A)(1) Exception (which requires (2) #6 screws or larger)

    Cheers, Wayne

  9. #9
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,944
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by wwhitney View Post
    Indeed, 314.27(A)(1) Exception (which requires (2) #6 screws or larger)

    Cheers, Wayne
    There it is, thanks
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  10. #10
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    2,489
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I sent a message to the GC asking the weight of the proposed fixtures.