    It has been my understanding the equipment grounding conductors should not be installed along with the service entrance conductors being installed to secondary compartment of the utility company’s
    pad-mounted transformers. Is that correct? Please advise thank you.
    Dan Craven
  2. #2
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    5,902
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Correct. There is a possibility that you could have a bonding jumper to something, but most of the time any bonding for say a pull box is done by bonding to the grounded conductor in the box.