Thread: Lockout/Tagout Disconnecting Means Within Sight

  1. #1
    Join Date
    Jun 2019
    Location
    Bethlehem, PA, USA
    Posts
    1
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Lockout/Tagout Disconnecting Means Within Sight

    Situation: Circuit breaker "Disconnecting Means" to deenergize equipment to be worked on is on a different floor, out of sight from the equipment to be worked on. The equipment to be worked on is a Main Disconnect Panel (which itself is a "Disconnecting Means") for a medical system, located in an equipment room adjoining the medical system. There is adequate space in the equipment room for a circuit breaker within line-of-sight of the Main Disconnect Panel.

    Questions:
    1. Is it an NEC code violation for the Disconnecting Means of this Main Disconnect Panel to not be within line-of-sight?
    2. Is the Disconnecting Means being within view of the equipment to be worked on required by the OSHA rules for lockout/tagout.
    3. Are there any other applicable codes or rules covering this?

    Comment: I see multiple instances of the phrase "disconnecting means shall be located within sight" in NFPA 70, including for motor controllers, carnival games, electric signs but none specifically for medical equipment.

    Thank you in advance.

  2. #2
    Join Date
    Apr 2019
    Location
    Union, KY, USA
    Posts
    248
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Don't most of the 'disconnecting means within site' include a exception for lockout/tagout capable?

    How does the AHJ verify the lockout/tagout actually gets used? Surprise inspections?? I'm assuming that would be OSHA, not NEC.

  3. #3
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,697
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    On any disconnect the line side will be live when it is in the open position. It sounds as if the existing "Main Disconnecting Panel" is all you need. Medical equipment is treated like the other items you mentioned as far as disconnecting means.

    Roger
    Moderator

  4. #4
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    8,742
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    If you were to need a disconnect within sight of a disconnect, where does it stop? What if you have to work on the in-sight disconnect? You would have a continuous string of disconnects in line-of-sight with each other then?

    No...

    The disconnect within sight is for machinery and equipment that might be serviced by NON electricians. It’s assumed that distribution systems themselves will only be opened and worked on by qualified electrical workers, who ostensibly know what they are doing.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...