    Kitchen counter pop-up receptacles

    A colleague asked me if it was Code compliant to install pop-up receptacles on a kitchen counter surface. My first response was that it was not. But, then I found these on the Internet :

    https://www.kitchenpowerpopups.com/p...caAjUKEALw_wcB

    Any thoughts on doing this and getting past an inspection. Obviously they will have to be GFCI protected.

  2. #2
    Join Date
    Jul 2007
    Location
    Iowegia
    Posts
    18,594
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    You might run afoul of getting it accepted due to it being plug-n-cord connected. 400.12.

    T&B used to make one that looks identical but was hard-wired. They discontinued them a few years back and it took me a lot of work to locate one for a hole in a c'top I had cut in.

  3. #3
    Join Date
    Feb 2003
    Location
    San Jose, CA
    Posts
    1,572
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Mockett makes several versions that are hardwired.
    https://www.mockett.com

    We just used this model for a project.
    https://www.mockett.com/power-commun...cs103a-ee.html
    Curt Swartz
    Electrical Contractor

  4. #4
    Join Date
    Jan 2016
    Location
    nj
    Posts
    232
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Article 400 only applies to cords that are listed under UL 62, refer to 400.1 and Informative Annex A. The cord that comes with the pop-up receptacle is most likely listed under UL 817 and is not a flexible cord or cable. This means that you are allowed to conceal the power cord, run through members, etc.

    Keep in mind what code cycle your municipality is under. The 2017 NEC corrected this discrepancy and placed cord sets and cord adapters under the scope of Article 400.

  5. #5
    Join Date
    May 2005
    Location
    St. Louis, Missouri
    Posts
    149
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The hangup can be is that the unit has to be UL listed as an assembly. Around St Louis this was debated very heavily by the AHJ and I think only the Hubbel unit was approved.

    http://ecatalog.hubbell-wiring.com/p...l_WLFTS004.pdf

    Check with you local AHJ before getting too far along

  6. #6
    Join Date
    Jan 2016
    Location
    nj
    Posts
    232
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jimmyglen View Post
    The hangup can be is that the unit has to be UL listed as an assembly. Around St Louis this was debated very heavily by the AHJ and I think only the Hubbel unit was approved.

    http://ecatalog.hubbell-wiring.com/p...l_WLFTS004.pdf

    Check with you local AHJ before getting too far along
    Same can be said about any product in that it needs to be listed for its use. I was merely trying to point out that NEC 400 shouldn't be applied to this product.

  7. #7
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,863
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by goldstar View Post
    A colleague asked me if it was Code compliant to install pop-up receptacles on a kitchen counter surface. My first response was that it was not. But, then I found these on the Internet :

    https://www.kitchenpowerpopups.com/p...caAjUKEALw_wcB

    Any thoughts on doing this and getting past an inspection. Obviously they will have to be GFCI protected.

    Yes it is compliant to have a pop up receptacle installed in the counter. However, if it is not direct wired someone could argue that the required outlet is under the counter and thus does not qualify as the compliant receptacle. The plug in version is really not much different than a plug strip.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  8. #8
    Join Date
    Feb 2007
    Location
    Highlands Ranch, CO
    Posts
    107
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I've used these. I see there is a direct wire and a cord connected.

    http://www.lewelectric.com/kitchen-c...ntertop-boxes/

  9. #9
    Join Date
    Apr 2019
    Location
    Union, KY, USA
    Posts
    303
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Anything popping out of a kitchen countertop is going to be filled with grunge in a matter of months, if not days! One good spill of pancake batter...

    How long will the 'pop-up' function continue to function without the spring breaking or rusting away? Then the only way to pop it up will be by sticking a knife in the gap around the fixture and prying it up.

  10. #10
    Join Date
    Dec 2011
    Location
    Wisconsin
    Posts
    681
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jeremy.zinkofsky View Post
    Article 400 only applies to cords that are listed under UL 62, refer to 400.1 and Informative Annex A. The cord that comes with the pop-up receptacle is most likely listed under UL 817 and is not a flexible cord or cable. This means that you are allowed to conceal the power cord, run through members, etc.

    Keep in mind what code cycle your municipality is under. The 2017 NEC corrected this discrepancy and placed cord sets and cord adapters under the scope of Article 400.
    400.12 does seem to apply to flexible cord sets and power supply cords.


    Informational Note: UL 817, Cord Sets and Power-Supply Cords,
    allows the use of flexible cords manufactured in accordance
    with UL 62, Flexible Cords and Cables. See 400.10 and 400.12 for
    flexible cords that are part of a listed cord set or power-supply
    cord.

    400.12 Uses Not Permitted. Unless specifically permitted in
    400.10, flexible cables, flexible cord sets, and power supply
    cords shall not be used for the following:
    (1) As a substitute for the fixed wiring of