Thread: General use receptacles on 30amp circuits

  1. #11
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,743
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    So you're asking about a single 15a receptacle on a 30a breaker?

    To me, that's worse than the same load shared by several receptacles on a 30a circuit.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  2. #12
    Join Date
    Jan 2011
    Location
    United States
    Posts
    9,374
    Mentioned
    1 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by LarryFine View Post
    So you're asking about a single 15a receptacle on a 30a breaker?

    To me, that's worse than the same load shared by several receptacles on a 30a circuit.

    No, between several to two dozen 15/20 amp receptacles on a 30 amp circuit.

  3. #13
    Join Date
    Jan 2007
    Posts
    4,219
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I've got another theory.

    Because the screw terminals are not rated for the larger wire, and, scabbing on a piece of #12 to a #10 to make it happen would be a code violation.

    JAP>

  4. #14
    Join Date
    Jul 2007
    Location
    Iowegia
    Posts
    18,620
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Are the terminals on a 15a device rated for #10?

  5. #15
    Join Date
    Jan 2011
    Location
    United States
    Posts
    9,374
    Mentioned
    1 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by jap View Post
    I've got another theory.

    Because the screw terminals are not rated for the larger wire, and, scabbing on a piece of #12 to a #10 to make it happen would be a code violation.

    JAP>

    You don't create one rule to prevent the violation of another- at least I believe that is the intent of the NEC.

  6. #16
    Join Date
    Jan 2007
    Posts
    4,219
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mbrooke View Post
    You don't create one rule to prevent the violation of another- at least I believe that is the intent of the NEC.
    What does that mean ??

    JAP>

  7. #17
    Join Date
    Jan 2011
    Location
    United States
    Posts
    9,374
    Mentioned
    1 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by jap View Post
    What does that mean ??

    JAP>
    Meaning the code would not limit receptacles to 20amp circuits because someone might violate 240.4 (D)

  8. #18
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,743
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mbrooke View Post
    No, between several to two dozen 15/20 amp receptacles on a 30 amp circuit.
    Then my original answer stands.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  9. #19
    Join Date
    Jan 2011
    Location
    United States
    Posts
    9,374
    Mentioned
    1 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by LarryFine View Post
    Then my original answer stands.

  10. #20
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,743
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mbrooke View Post
    I had said:
    Quote Originally Posted by LarryFine View Post
    My electrical theory is that 30a requires more metal in the current-carrying parts than 15/20a devices are made with, and OCPDs can't reliably protect the devices from overload damage.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA