Thread: General use receptacles on 30amp circuits

  1. #21
    Join Date
    Jan 2011
    Location
    United States
    Posts
    9,362
    Mentioned
    1 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by LarryFine View Post
    I had said:


    But are you going to see 4,400 to 4,600 watts of load on it? Doubt it.


    Ultimately 20amp OCPDs would be used, but the real world is different.

  2. #22
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,723
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mbrooke View Post
    But are you going to see 4,400 to 4,600 watts of load on it? Doubt it.
    To help us understand your thoughts a little better, why would the same not be able to be said about any device on any circuit?

    Why not ask: "Why shouldn't we be able to wire 15/20a receptacles on a 60a circuit?" What's different in your example?
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  3. #23
    Join Date
    Jan 2007
    Posts
    4,211
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mbrooke View Post
    But are you going to see 4,400 to 4,600 watts of load on it? Doubt it.


    Ultimately 20amp OCPDs would be used, but the real world is different.
    But, couldn't we apply that train of thought to most any Device/OCPD combination if we wanted too?

    Why try and reinvent the wheel?


    Jap>

  4. #24
    Join Date
    Jan 2011
    Location
    United States
    Posts
    9,362
    Mentioned
    1 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by LarryFine View Post
    To help us understand your thoughts a little better, why would the same not be able to be said about any device on any circuit?

    Why not ask: "Why shouldn't we be able to wire 15/20a receptacles on a 60a circuit?" What's different in your example?
    A short circuit might melt the plug to appliance flex cord before the breaker trips, if at all.

  5. #25
    Join Date
    Jan 2011
    Location
    United States
    Posts
    9,362
    Mentioned
    1 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by jap View Post
    But, couldn't we apply that train of thought to most any Device/OCPD combination if we wanted too?

    Why try and reinvent the wheel?


    Jap>
    Unfortunately reinventing the wheel is the norm
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	power layout 1.jpg 
Views:	56 
Size:	143.6 KB 
ID:	23123   Click image for larger version. 

Name:	power layout 2.jpg 
Views:	43 
Size:	157.1 KB 
ID:	23124  

  6. #26
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,723
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mbrooke View Post
    A short circuit might melt the plug to appliance flex cord before the breaker trips, if at all.
    Same with a lamp cord on a 30a circuit.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  7. #27
    Join Date
    Jan 2011
    Location
    United States
    Posts
    9,362
    Mentioned
    1 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by LarryFine View Post
    Same with a lamp cord on a 30a circuit.
    But not for a 20?

  8. #28
    Join Date
    Jan 2011
    Location
    United States
    Posts
    9,362
    Mentioned
    1 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by jap View Post
    But, couldn't we apply that train of thought to most any Device/OCPD combination if we wanted too?

    Why try and reinvent the wheel?


    Jap>
    Ignore "special purpose" its a office cubical receptacle
    Attached Images Attached Images  

  9. #29
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,723
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mbrooke View Post
    But not for a 20?
    I'd rather see a #18 on a 20a breaker than on a 30a.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  10. #30
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,723
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mbrooke View Post
    Ignore "special purpose" its a office cubical receptacle
    Is this a question about the #10 neutral some partition wiring includes?

    Or do you want to reduce the quantity of circuits to feed cubicle wiring?
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA