Thread: Occ Sensor Control Wiring in same conduit with 277 volt lighting circuit?

  1. #1
    Join Date
    Nov 2015
    Location
    MN
    Posts
    18
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Occ Sensor Control Wiring in same conduit with 277 volt lighting circuit?

    I understand that if it's 0-10v dimming circuit, it's considered class 1, and needs to be separate from power conductors....but how about the "low voltage" control conductors going to an occupancy sensor?

  2. #2
    Join Date
    Nov 2015
    Location
    MN
    Posts
    18
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Sorry....for clarification...I believe the 0-10v dimming conductors are considered class 2 circuits. My previous post said class 1.

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,496
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    The LV occupancy sensors that we install are Class 2 so their conductors cannot go in the same raceway as the power conductors. Some 0-10 volt lighting control can be reclassified as Class 1 and occupy the same raceway as the power conductors.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #4
    Join Date
    Nov 2018
    Location
    New Orleans, LA
    Posts
    20
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    You can put low voltage wiring in the same condiut as power conductors as long as the low voltage wiring is rated for 600V (i.e. you could use some #14 THHN)

  5. #5
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    4,821
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Johnhall30 View Post
    You can put low voltage wiring in the same condiut as power conductors as long as the low voltage wiring is rated for 600V (i.e. you could use some #14 THHN)
    That is not correct.

    -Hal

  6. #6
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,496
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Johnhall30 View Post
    You can put low voltage wiring in the same condiut as power conductors as long as the low voltage wiring is rated for 600V (i.e. you could use some #14 THHN)

    That's a common misconception, Class 2 circuits that cannot be reclassified as Class 1 cannot be in the same raceway regardless of the voltage rating of the conductors.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  7. #7
    Join Date
    Nov 2015
    Location
    MN
    Posts
    18
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    ...unless it's in luminaire cable! I wonder how that is acceptable?

  8. #8
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    20,349
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Lbartowski View Post
    ...unless it's in luminaire cable! I wonder how that is acceptable?
    That is acceptable because of the separate jacket around the Class 2 conductors.
    The argument is similar to the argument that two sets of wires, each inside their own EMT or Smurf tube, do not create a violation when those two raceways are run through a common enclosing raceway.

    Sent from my XT1585 using Tapatalk

  9. #9
    Join Date
    Nov 2015
    Location
    MN
    Posts
    18
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Right, but is luminaire cable really 2 separate raceways just because the control cable is jacketed? That logic would seem to allow me to pull a jacketed control cable (like an 18/3) within an EMT with 277 volt circuits then right?

  10. #10
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    20,349
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Lbartowski View Post
    Right, but is luminaire cable really 2 separate raceways just because the control cable is jacketed? That logic would seem to allow me to pull a jacketed control cable (like an 18/3) within an EMT with 277 volt circuits then right?
    Right. If the control cable is a self-contained wiring method that does not require a raceway, it should be able to share the enclosing raceway. But without the explicit UL listing that luminaire cable has, an inspector may not agree.