mstrlucky74
Senior Member
- Location
- NJ
scenario.... you have a panel 150' from work space and have to run (3) 120v 20a ckts to the area and don't want to use multipole breaker or handle ties. would you run EMT with those 3 ckts all the way from the panel to the space or just right out of the panel about 10' to a box then run 3 separate 10/2 Mc cables the rest of the way? I think cables would be quicker and easier.