    Derating

    I have (4)-20 amp double pole breakers feeding lights that doesn’t have a neutral. Can I use the 8 #12 current carrying conductors in a 3/4 conduit or do need to go to #10s to derate?

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,534
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Yes derating is required because you have more than 3 CCC in a single raceway. Good news is that you can still use #12 AWG conductors.

    #12 THHN = 30 amps @90 degrees C
    30 amps*70% = 21 amps adjusted ampacity.

    Welcome to the forum.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,754
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    To follow Robs reasoning, depending on the insulation type of the conductors see article sections 110.14(C), 310.15(B)(3)(a), and 310.15(B)(16).

    Roger
    Moderator

  4. #4
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,534
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Yes, I did make some assumptions with the 90 degree C conductor. A 75 degree C conductor might also work if you can apply the next size up rule.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted