    Megger or Replace cable

    Hi folks,

    We're replacing a low voltage air compressor that has been in service for around 50 years at an industrial plant. Would you recommend megger testing the feed or pulling a new cable? The distance is about 70 feet from MCC to the unit.

    Thanks,
    EE

  2. #2
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    2,486
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by FaradayFF View Post
    Hi folks,

    We're replacing a low voltage air compressor that has been in service for around 50 years at an industrial plant. Would you recommend megger testing the feed or pulling a new cable? The distance is about 70 feet from MCC to the unit.
    My gut says replace it but you will need to do a cost benefit analysis to get a definitive answer that question i.e. [cost to replace cable] vs. [cost to test cable] + [cost to replace cable] x odds it has failed stated as a decimal from .00 to 1.00.

    Make sure you take all the labor and material costs into account for an accurate analysis. (Including the difficulty of running the cable.)

    You could also do nothing and replace it when it fails. This might be the least expensive solution if downtime is allowed.

  3. #3
    Join Date
    Jun 2003
    Location
    NE (9.06 miles @5.9 Degrees from Winged Horses)
    Posts
    11,401
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    We did a sound analysis of feeders for some pellet mills. I had the CEO listen as I bent the wires in a gutter. The sound of the old rubber insulation cracking was enough. It most likely would have passed a megger test as the area was dry and they had had no issues.
    Tom
    TBLO

  4. #4
    Join Date
    Jul 2006
    Location
    Roughly 5346 miles from Earls Court
    Posts
    2,882
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    I had the CEO listen as I bent the wires in a gutter. The sound of the old rubber insulation cracking was enough. It most likely would have passed a megger test as the area was dry and they had had no issues.
    And they might meg out fine until they're being bent around to connect the new compressor. If it's a fairly easy pull, I'd just replace them.

    What size are we talking about? Heck of a difference between replacing 10g and 2g.

  5. #5
    Join Date
    Mar 2003
    Location
    New York
    Posts
    1,940
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    In a nuke you megger new wire.

  6. #6
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    2,486
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by sameguy View Post
    In a nuke you megger new wire.
    Not only nukes. I've seen many new switchgear installs get megged. Last thing you want is all that new equipment blowing up due to a bad conductor.

  7. #7
    Join Date
    Aug 2009
    Location
    Tacoma, Wa
    Posts
    549
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Coppersmith View Post
    Not only nukes. I've seen many new switchgear installs get megged. Last thing you want is all that new equipment blowing up due to a bad conductor.
    It is in our spec to meg all new circuit conductors--Done that all my career--just makes sense--only takes seconds to meg a conductor
    RichB N7NEC

  8. #8
    Join Date
    Jun 2003
    Location
    NE (9.06 miles @5.9 Degrees from Winged Horses)
    Posts
    11,401
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by FaradayFF View Post
    Hi folks,

    We're replacing a low voltage air compressor that has been in service for around 50 years at an industrial plant. Would you recommend megger testing the feed or pulling a new cable? The distance is about 70 feet from MCC to the unit.

    Thanks,
    EE
    Define low voltage. What HP?
    Tom
    TBLO

  9. #9
    Join Date
    Jan 2018
    Location
    California
    Posts
    46
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    20 HP unit.

  10. #10
    Join Date
    Jun 2003
    Location
    NE (9.06 miles @5.9 Degrees from Winged Horses)
    Posts
    11,401
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by FaradayFF View Post
    20 HP unit.
    That's #8 at 480v. It cost more to talk about it than pull new wire. Depending on what your work procedures are, of course. Is there easily scheduled down time?
    Tom
    TBLO