    arc fault breakers


    the home inspector doing these new homes I am doing says you don't need arc fault breakers where there is gfci protection like on the disposal or dishwasher, kitchen counter where there are gfci's protecting those appliances. So like if I have a gfci outlet in the garage protecting the outlets there he says no need for arc fault breaker have you any input?

  2. #2
    Join Date
    Jul 2007
    Location
    Iowegia
    Posts
    18,590
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Said 'home inspector' needs to re-read 210.12.

  3. #3
    Join Date
    May 2014
    Location
    Marlborough, Massachusetts USA
    Posts
    403
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    those home inspectors....

  4. #4
    Join Date
    Jul 2007
    Location
    Iowegia
    Posts
    18,590
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Knuckle Dragger View Post
    those home inspectors....
    Proud graduate of the Class of Tuesday, 9:30 AM.

  5. #5
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    4,821
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by enireh View Post

    the home inspector doing these new homes I am doing says you don't need arc fault breakers where there is gfci protection like on the disposal or dishwasher, kitchen counter where there are gfci's protecting those appliances. So like if I have a gfci outlet in the garage protecting the outlets there he says no need for arc fault breaker have you any input?
    If you are on the 1984 code cycle like your profile says you don't need any AFCIs.

    -Hal

  6. #6
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,718
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by enireh View Post

    the home inspector doing these new homes I am doing says you don't need arc fault breakers where there is gfci protection like on the disposal or dishwasher, kitchen counter where there are gfci's protecting those appliances. So like if I have a gfci outlet in the garage protecting the outlets there he says no need for arc fault breaker have you any input?
    Home inspector (privately hired by home buyer with no legal power) or building inspector (government employee with quite a bit of legal power)?
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  7. #7
    Join Date
    Apr 2005
    Location
    Atlanta,GA
    Posts
    6,459
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by enireh View Post

    the home inspector doing these new homes I am doing says you don't need arc fault breakers where there is gfci protection like on the disposal or dishwasher, kitchen counter where there are gfci's protecting those appliances. So like if I have a gfci outlet in the garage protecting the outlets there he says no need for arc fault breaker have you any input?

    "New homes" or any "new work" needs to be wired according to the latest code cycle adopted by the jurisdiction where you are working.

    There have been a lot of changes on arc fault protection needed in the last few years.

    So what code cycle are you working under?
    The 95% of people that you can't trust give the other 5% a bad name.

  8. #8
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,565
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by enireh View Post

    the home inspector doing these new homes I am doing says you don't need arc fault breakers where there is gfci protection like on the disposal or dishwasher, kitchen counter where there are gfci's protecting those appliances. So like if I have a gfci outlet in the garage protecting the outlets there he says no need for arc fault breaker have you any input?
    At one time that was somewhat a general rule that you could rely on to some extent. If it didn't require GFCI protection it probably required AFCI protection. But 2014 and 2017 NEC that logic is completely useless. That logic still had some holes in it but it sort of worked most of the time when applying it to 2008 and 2011 NEC.
    I live for today, I'm just a day behind.

  9. #9
    Join Date
    Jul 2007
    Location
    Iowegia
    Posts
    18,590
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    . But NEC logic is completely useless.
    Fify.

  10. #10
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,565
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by 480sparky View Post
    Fify.