    2500a bussed ct

    does the EC normally install the line side of the bussed CT if its feed from a service gutter?

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,534
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    We always do. We just do not connect the Ct's leaving the meter wire for the POCO but we wire the meter pan.

    Here's a 2000 amp service we just did with a 10 point meter pan. Click image for larger version. 

Name:	20190521_081403.jpg 
Views:	91 
Size:	142.0 KB 
ID:	23160
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    4,837
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Weird place for that meter pan and how do you get the cover off that LB?

    -Hal

  4. #4
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,534
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by hbiss View Post
    Weird place for that meter pan and how do you get the cover off that LB?

    -Hal
    I agree but that was the only place in the closet that the meter pan would fit. The photo is deceiving there is about 6" of space between the LB and the cabinet next to it which was enough room to pull the 10-point meter cable in and install the cover.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  5. #5
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,744
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    . . . 10-point meter cable . . .
    Please tell us more about that cable.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  6. #6
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,534
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    Please tell us more about that cable.
    It's a Con Ed specification cable, 10 conductors (10 point) all #9 AWG stranded conductors. Yup that is correct, each conductor is labeled #9 AWG with a special 10-point meter color code.

    Click image for larger version. 

Name:	20190521_083646.jpg 
Views:	26 
Size:	144.2 KB 
ID:	23164
    Last edited by infinity; 06-25-19 at 11:11 AM. Reason: Added Photo
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •