    Two family with house meter bond and grounding question.

    Hi
    I am working on a two family house with three gang meter sockets. three 100 amp main breaker panels .
    I am replacing one panel so have to upgrade grounding. my question is where does water main ground go? To the first panel neutral bar? and ground rod to all panels in and out from neutral to neutral and does it have to be continuous unbroken. from panel to panel. what are my options? Thank you in advance

  2. #2
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    10,116
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by digitaltwist View Post
    Hi
    I am working on a two family house with three gang meter sockets. three 100 amp main breaker panels .
    Three meter sockets in one common enclosure? Where is the service disconnect in relation to the main breaker panels?

    I am replacing one panel so have to upgrade grounding. my question is where does water main ground go? To the first panel neutral bar? and ground rod to all panels in and out from neutral to neutral and does it have to be continuous unbroken. from panel to panel. what are my options? Thank you in advance
    Upgrade why? What is there now?
    If you don't think too good, don't think too much.

  3. #3
    Join Date
    Jan 2007
    Posts
    5
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    YES Three meter sockets in one common enclosure.
    NO service disconnect. Each panel is feed from the meter enclosure and all three panel have 100 amp main breakers.

  4. #4
    Join Date
    Jan 2007
    Posts
    5
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The code applied here is nyc code.

  5. #5
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,919
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by digitaltwist View Post
    Hi
    I am working on a two family house with three gang meter sockets. three 100 amp main breaker panels .
    I am replacing one panel so have to upgrade grounding. my question is where does water main ground go? To the first panel neutral bar? and ground rod to all panels in and out from neutral to neutral and does it have to be continuous unbroken. from panel to panel. what are my options? Thank you in advance
    See 250.64(D). That gives you the options for the earthing connections for multiple service disconnect enclosures. I generally find the "common location" method made in the meter to be the easiest for multi gang sockets without disconnects
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  6. #6
    Join Date
    Jan 2007
    Posts
    5
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    meter socket grounding work for me in this case.
    any other suggestions?

  7. #7
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,919
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by digitaltwist View Post
    meter socket grounding work for me in this case.
    any other suggestions?
    I don't have any further suggestions. Do you have a specific question?
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"