Thread: Two conductors feeding tenant

  1. #11
    Join Date
    Jun 2018
    Location
    Glen bunie, md, us
    Posts
    635
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Right. What I meant was post #1 sketch if the tenant space had fire and someone had to shut off all power to that tenant space but was not able to get into the tenant space then that person would have to go to electric room to shut off power and he would not know their are two breakers feeding the tenant space.

    Code does not say anything regarding placement of labels telling which breaker(s) feed which tenant space in situation attached sketch post #1?

  2. #12
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,629
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Bottom line, there is no Code provision that prohibits multiple feeders to a tenant space, Diligence to 110.22 should result in labeling that addressed the multiple feed (such as "Supply 1 of 3 to Suite 104", etc)