    Two conductors feeding tenant

    Attached sketch shows service entrance switchboard with six service disconnects inside mall electric room. From the switchboard their is two serivce disconnects that feed from the electic room all the way to second floor tenant room to disconnect #1 main to trough and disconnect #2 to P1. From trough their is tapped disconnect which feeds Xfmr P2. All tenant equipment is grouped in one room.

    Question is can you have two service disconnects feeding one tenant as shown on sketch? If yes then what is code section and if no then what is the code section?

    Sent from my SM-G935U using Tapatalk

  2. #2
    Join Date
    Feb 2003
    Location
    Seattle, WA
    Posts
    19,648
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by hhsting View Post
    Question is can you have two service disconnects feeding one tenant as shown on sketch? If yes then what is code section and if no then what is the code section?
    Yes. Code reference is article 100. The two disconnects to which you refer are not "SERVICE" disconnects, as that word is defined in article 100. So the prohibition of having more than one "service" to a building, as provided in 230.2, does not apply.

    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.

  3. #3
    Join Date
    Jun 2008
    Location
    Dallas, Tx
    Posts
    624
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yes… 230.2

  4. #4
    Join Date
    Jun 2008
    Location
    Dallas, Tx
    Posts
    624
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by charlie b View Post
    Yes. Code reference is article 100. The two disconnects to which you refer are not "SERVICE" disconnects, as that word is defined in article 100. So the prohibition of having more than one "service" to a building, as provided in 230.2, does not apply.


  5. #5
    Join Date
    Jun 2018
    Location
    Glen bunie, md, us
    Posts
    635
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Ok two 200A breakers are service disconnects since their is no main breaker and has incoming electric utility service. No?

    Load side of two 200A breakers are feeders. So what about two feeders going into same tenant space? Isnt their restriction that only one feeder feed tenant space?
    Last edited by hhsting; 07-11-19 at 04:10 PM.

  6. #6
    Join Date
    Jun 2018
    Location
    Glen bunie, md, us
    Posts
    635
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Does post #1 sketch comply per NEC 2014 Article 230.40 exceptions? I have two service entrance conductor going to one occupancy instead of one no?

    Sent from my SM-G935U using Tapatalk

  7. #7
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    4,831
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    After the service disconnect at the meters you have feeders going to the tenant space. This might have been two separate spaces that were combined into one. I see no problem.

    -Hal

  8. #8
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,629
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Best ref is likely 225.30. Only on feeder to a building or other structure. As long as all the equipment is located in one building (See Art 100) you can have as many feeders/branches as you like.
    (might check 240.24 also)
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  9. #9
    Join Date
    Jun 2018
    Location
    Glen bunie, md, us
    Posts
    635
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    In the event of fire someone goes in to electric room thinking one disconnect is feeding space but there are two. All this is inside the building and code does not even enforce labels. 225 is for outside feeders all this is inside mall.

    Sent from my SM-G935U using Tapatalk

  10. #10
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    10,116
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by hhsting View Post
    In the event of fire someone goes in to electric room thinking one disconnect is feeding space but there are two. All this is inside the building and code does not even enforce labels. 225 is for outside feeders all this is inside mall.

    Sent from my SM-G935U using Tapatalk
    If you want to be taken seriously, get good, answers, and not be accused of trolling you need to pay more attention to grammar and punctuation. It doesn't have to be perfect, mine isn't, but the post above is almost indecipherable.

    Besides, it's just good manners.
    If you don't think too good, don't think too much.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •