    Insulation piercing connectors

    I’m using these for reference voltage for monitoring modules, tapping into line and load side of ATS’s. First time using them, and they’re pretty slick. I’ve used a few different sizes so far, including the big boys of 750 - 4/0 main with a 10-14 tap range. I’m installing in-line fuses with each tap, between the connector and the tap conductor. I’m curious though, would this fall into the NEC tap rules?

  2. #2
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    20,350
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    IMHO, the conductors from the tap connector to the inline fuse would be considered tap conductors while the listed tap connector itself is likely not. But an inspector may not have a problem with a short length having too high a current ratio for tap rule compliance. Any one with experiences to report?

    Sent from my XT1585 using Tapatalk

  3. #3
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,732
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    It's done all the time for the voltage taps when using CTs.

    Don't know if that addresses the code-compliance question.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  4. #4
    Join Date
    Jul 2003
    Posts
    105
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It's a judgement call but it's not really a current carrying conductor. Milliamps to the voltage sensor.

    Sent from my SM-T350 using Tapatalk

  5. #5
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    11,225
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by rdubamos View Post
    I’m using these for reference voltage for monitoring modules, tapping into line and load side of ATS’s. First time using them, and they’re pretty slick. I’ve used a few different sizes so far, including the big boys of 750 - 4/0 main with a 10-14 tap range. I’m installing in-line fuses with each tap, between the connector and the tap conductor. I’m curious though, would this fall into the NEC tap rules?
    We use them for supply side connected PV (solar) systems nearly all the time. They fit inside the MDP and they don't require a shutdown. Yeah, they are pretty slick.