User Tag List

Results 1 to 2 of 2

Thread: Do hardwired car chargers require disconnect or not?

  1. #1
    Join Date
    Jul 2019
    Location
    machu picchu
    Posts
    1
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Do hardwired car chargers require disconnect or not?

    I am not clear whether a hardwired electrical car charger requires a AC disconnect or not. i.e. a 60A 240V Tesla charger.
    I imagine if plugged into NEMA 14-50 i would not. But not sure about hardwired for installation within a garage.

  2. #2
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,872
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    Welcome to the forum.

    Unless the charger is larger than 60 amps then no disconnect is required


    625.43 Disconnecting Means. For equipment rated more than
    60 amperes or more than 150 volts to ground, the disconnecting
    means shall be provided and installed in a readily accessible
    location. The disconnecting means shall be lockable open in
    accordance with 110.25.