FMC in Elevator Machine Room

Status
Not open for further replies.

cvirgil467

Senior Member
Location
NewYork
I noticed FMC being used as the main feeder to an elevator from a distribution board. The feeder (in FMC) is routed from a distribution board and terminates in a disconnect switch in the elevator machine room.

Per the 2005 NEC section 620.21(3) - i think this might be a violation unless the distance limitations noted are only related to the liquidtight.

Any thoughts?

Thanks.
C
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Note 620.21(A)(3) is only addressing from the load side of the disconnect.

Roger
 

dcspector

Senior Member
Location
Burke, Virginia
I noticed FMC being used as the main feeder to an elevator from a distribution board. The feeder (in FMC) is routed from a distribution board and terminates in a disconnect switch in the elevator machine room.

Per the 2005 NEC section 620.21(3) - i think this might be a violation unless the distance limitations noted are only related to the liquidtight.

Any thoughts?

Thanks.
C

Key word within "Machine Rooms" and the exception is "LFNC" and 6' is the limitation on FMC within the "Machine Room"
 
Last edited: