fire alarm detector inside shower or bath

Status
Not open for further replies.

wbalsam1

Senior Member
Location
Upper Jay, NY
Within the shower zone or bathtub zone seems like a terrible place to locate an alarm/detector since the superheated air would trigger just about any alarm/detector. Maybe a rate-of-rise in a large enough bathroom away from showers and tubs. Check NFPA 72. :)
 

RICK NAPIER

Senior Member
Location
New Jersey
According to the National Fire Alarm Code NFPA 72 smoke detectors are not permitted in areas above 92% humidity unless specifically designed for the use and in residential uses are required to be 3 feet away from bathrooms.
 

nakulak

Senior Member
I've often thought of installing a flame detector in my bathroom in case I was to spontaneously combust while taking a shower.
 

wbalsam1

Senior Member
Location
Upper Jay, NY
I've often thought of installing a flame detector in my bathroom in case I was to spontaneously combust while taking a shower.
Don't worry. The water should dowse any flames as quickly as they appear. Just shower with the water on at full force just to be safe.:D
 

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
I've often thought of installing a flame detector in my bathroom in case I was to spontaneously combust while taking a shower.

Well the fire dept. would call it an "electrical fire" and blame you anyhow. :smile:
 

480sparky

Senior Member
Location
Iowegia
Don't worry. The water should dowse any flames as quickly as they appear. Just shower with the water on at full force just to be safe.:D

Wow. You must take some really long showers. 24 hours every day?
giggle.gif
 