underground service meter grounding

Status
Not open for further replies.

mikey p

New member
If you are upgrading a meter in a commercial location, where the meter has a main breaker in its inclosure, do you need to bring all the grounds to the meter bank or the first sub panel off the main breaker?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
If you are upgrading a meter in a commercial location, where the meter has a main breaker in its inclosure, do you need to bring all the grounds to the meter bank or the first sub panel off the main breaker?

The grounding electrode conductor(s) must be connected to the grounded conductor at or ahead of the service disconnecting means. Take a look at 250.24(A)(1).

Chris
 