Hey guys heard a myth that you cant have feeders and branch circuits in the same conduit is this true? What I ended up having was an existing 11/4 conduit feeding a panel on a raised stage. We could not easily get into the panel. So we traced conduit out and found a jbox which we used to pull our new branch circuits. Pipe fill was not violated any other problems?
 

TOOL_5150

Senior Member
Location
bay area, ca
Hey guys heard a myth that you cant have feeders and branch circuits in the same conduit is this true? What I ended up having was an existing 11/4 conduit feeding a panel on a raised stage. We could not easily get into the panel. So we traced conduit out and found a jbox which we used to pull our new branch circuits. Pipe fill was not violated any other problems?

feeders and branches can be in the same conduit, the issue would be service conductors and feeders/branches in the same conduit.

The only thing you have to make sure is pipe fill and derating issues [if any]

~Matt
 