GFCI protection in woodwork factory.

Status
Not open for further replies.

Chamuit

Grumpy Old Man
Location
Texas
Occupation
Electrician
Is GF protection required for general service receptacles in a woodworking factory? The receptacles are to be used at assembly tables.

I looked through 210.8 and Commetary Table 210.1 (2005) and didn' see anything.
 

Bea

Senior Member
There are no requirements in 210.8(B) that would require them or in 502 or 503 whichever class the area is. Unless there are local amendments that would require GFCI protection it is not required.
 

Chamuit

Grumpy Old Man
Location
Texas
Occupation
Electrician
The area does not meet the requirements of 502. This came issue up with the city and NEMA 4X is not required.
 