    I need to have multiple runs of 14/2 or 14/3 to end in a minimum 2 gang box. I am debating a 2 gang metal box with and extension on it (2x6 walls) or would you use a 3 gang (not sure the cu inches) with a reducing cover to 2 gang. I am looking for 46 cu inches.
    Any thoughts?
    c2500
  2. #2
    Join Date
    Jan 2004
    Right here.
    Posts
    12,326
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    A deep 4-11 (42 cubic inches) and a 2-gang mud ring (6.3 cubic inches) will get you what you need.
  3. #3
    Join Date
    Jan 2008
    NC & IN
    Posts
    3,530
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Check out 314.16 and the table their , too.
  4. #4
    Join Date
    May 2008
    Posts
    3
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I opt to go with regular depth 1900 bracketed, with the extension then ring. I've also done the 11B many many times