The equipment in question here is a shake machine at a fast food restaurant. For as long as I’ve been doing them, the plans have always specified a 50/3 circuit.
I’m currently doing a lot of remodels in Florida, and just got flagged on this as apparently the nameplate specifies a 45/3 MOCP. This was a relocation of an existing machine using the existing 50/3 circuit. This job was permitted on the 2014 NEC, but I’ve got several more in this town all permitted after 1/1/2021, so the 2017 NEC will apply.
As far as I can see, no one makes a 45/3 GFCI. Most of these stores have either Square D or Westinghouse gear. Eaton doesn’t even make a 3-pole GFCI breaker in any size, and my original plan was to install SqD sub panel with a 50/3 GFCI, which is what every new store uses. Inspector is telling me to figure it out.
I suppose my only option is to install a disconnect with a 45/3 breaker fed by a 50/3 GFCI? Any other thoughts? The “next size up” rule doesn’t apply to cord and plug equipment. I’ve been building these stores for over 10 years and this is the first time I’ve ran into this issue. I’m going to send this up the chain to corporate engineering also and get their thoughts.
Sent from my iPhone using Tapatalk
I’m currently doing a lot of remodels in Florida, and just got flagged on this as apparently the nameplate specifies a 45/3 MOCP. This was a relocation of an existing machine using the existing 50/3 circuit. This job was permitted on the 2014 NEC, but I’ve got several more in this town all permitted after 1/1/2021, so the 2017 NEC will apply.
As far as I can see, no one makes a 45/3 GFCI. Most of these stores have either Square D or Westinghouse gear. Eaton doesn’t even make a 3-pole GFCI breaker in any size, and my original plan was to install SqD sub panel with a 50/3 GFCI, which is what every new store uses. Inspector is telling me to figure it out.
I suppose my only option is to install a disconnect with a 45/3 breaker fed by a 50/3 GFCI? Any other thoughts? The “next size up” rule doesn’t apply to cord and plug equipment. I’ve been building these stores for over 10 years and this is the first time I’ve ran into this issue. I’m going to send this up the chain to corporate engineering also and get their thoughts.
Sent from my iPhone using Tapatalk