zcanyonboltz

Senior Member
Location
denver
I am doing a service change where an all in one panel has an ac in it then feeds a sub panel with SER in house with the rest of breakers. I am aware since the whole house is not fed from the sub panel feed because of AC in main I must use a breaker that is rated to same or less than the SER. Can i splice the SER in panel to go from 2/0 aluminum to #1 copper since 2/0 wont fit under a 125 amp breaker? Something is making me wonder if its legal to splice the sub feed? # 1 copper is rated to 130 amps and 2/0 aluminum to 135 so I know my wire sizes are rated to at least 125 amps. Thanks
 
Yes you can splice but do you need to? I know 125 amp Square D HOM, Eaton BR and Siemens Q are listed for up to 2/0. Are you installing the SER new? If so why not use 1/0? Unless you calculated load is over 120 amps 1/0 is fine with 125 amp over current protection.
 
I am doing a service change where an all in one panel has an ac in it then feeds a sub panel with SER in house with the rest of breakers. I am aware since the whole house is not fed from the sub panel feed because of AC in main I must use a breaker that is rated to same or less than the SER. Can i splice the SER in panel to go from 2/0 aluminum to #1 copper since 2/0 wont fit under a 125 amp breaker? Something is making me wonder if its legal to splice the sub feed? # 1 copper is rated to 130 amps and 2/0 aluminum to 135 so I know my wire sizes are rated to at least 125 amps. Thanks
You are misunderstanding 310.12. Your feeder conductors are allowed to be sized using 310.12 even if you have some of your load at the meter/main because the feeder conductors are never required to be larger than the service conductors. See 310.12(C).
For example if you have a 150 amp meter/main with spaces for breakers and feed through lugs you can use 2/0 AL for the service conductors and the feeder even if you have loads fed from breakers on the bus in the meter/main.
 
After rereading the OP I get the sense that maybe you are putting a 125 amp branch breaker in a main panel that is larger than 125 amp. If that is the case, then you are correct that you can not use 310.12 allowances. For example if you have a 200 amp main panel with a 125 amp branch breaker you will need conductors for that feeder to be sized per Table 310.16.
My comments in my previous post were assuming that you had a feed through meter main.
 