designer82
- Boston
Working on a commercial building, 4 floors. Each floor is roughly 8,500 sq.ft.
2nd floor was previously only business, now it’s split into business & R-4 Residential.
The R-4 Residential space has a bunch of sleeping rooms with a shared common corridor and common living rm./kitchen.
I added a bunch of smoke/co detectors in the R-4 space for the sleeping units.
There’s a question regarding alarming. Initially I had noted to program it such that: Any initiation device within a sleeping room alarms only the sleeping room and sends supervisory signal. But now the architect is saying this is actually a “dwelling unit” since there’s a shared kitchen/living rm.
Would it make more sense to program to alarm the entire R-4 space if initiation of any device in any of the sleeping rooms?
Or stick with alarming just the affected sleeping room?
Also, initiation of a common device in R-4 area (common corridor/living/kitchen)… would it make more sense to alarm just the R-4 area in that case or whole building?
Thank you
Thank you