behindpropellers
- NE Ohio
- Mechanical Engineer
Hello,
We have a 15KVA transformer that was installed for a 200A service. It previously had a 100A service that was installed directly to the panel in the building which was too small. I had an electrician install a sub-panel adjacent to the transformer and we ran the branches off of that. I asked him to install 200A service into the building.
After asking for the 200A service I was out at the jobsite a few days later and he had installed a 125A service.
Is there a technical reason to why they did not do what I asked them to do?
Other issues I am having with this contractor:
1. Main leg into panel was not torqued down.
2. Loose grounds in job box next to receptacle.
3. Ground rod was sticking out of the ground (hazard). I pounded it down and found the ground clamp was loose.
4. Electrician didn't tell me I needed a EE PE to sign off service changes prior to starting the job.
5. Panel installed has a manufacturing defect.
I'm frustrated that I hired an "expert" and I am now reading regulations to find out what they messed up.
Tim
PS - The conduit connecting panels is 2" PVC. 1/0 ALU conductors with a #4 AL ground.
Tim