Got an installation that I need to replace the main panel. There is an exterior disconnect a solar system that feeds a power wall and for back feed and power wall acts a generator when primary power is off. Question is what is the shut down sequence to eliminate all power without causing an issue to the PV and power wall? Or does it matter?
There is likely a micro grid interconnect device (a transfer switch) as well. Shutdown and startup sequence can change slightly with different inverters, but generally for a hybrid system with battery backup it is:
Place inverter in standby or off mode with any logical switch it might have.
Turn off battery logically if it has that capability.
Turn off DC disconnect to battery
Turn off DC disconnect on inverter
Put transfer switch in bypass so critical loads can be grid powered, if it has that capability.
Turn off AC disconnect between grid and inverter
Turn off any backed breaker the inverter may be landed on.
Some systems are installed with a rapid shutdown switch for the PV inverter and some have an emergency disconnect or remote switch for the battery.
If you post what make and model of inverter and any MID or transfer switch maybe we can provide more detailed guidance.
Then lock out and tag out and check v