I am not sure if the following installation is in code compliance.
Details:
A. 300A fused disconnect on vertical busduct feeds 300A feeder in trough (277/480V system).
B. 70A tap conductors connect to this 300A feeder.
C. Tap conductors land on 70A branch breaker in Panel HV-1.
D. Panel HV-1 is main lug type with 100A bus rating.
My question: Can this 70A branch circuit breaker properly serve as the main OCPD for the panel?
Looking for code clarification and practical experience. Thanks.
Picture are attached for visualization.