A Alwayslearningelec Senior Member Location NJ Occupation Estimator Jun 19, 2025 #1 I have no panel schedule and going to ask vendor to budget. With the info below the panel would have to be at least 400A, correct?
I have no panel schedule and going to ask vendor to budget. With the info below the panel would have to be at least 400A, correct?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jun 19, 2025 #2 Since the OCPD is 400 amps the panel would need to be rated for at least 400 amps.
Fred B Senior Member Location Upstate, NY Occupation Electrician Jun 19, 2025 #3 Given the 400A fused disconnect before the MB Panel and no indications of a split system with 2-200A and showing 600 MCM wire and presuming CU conductors as it is not indicated, I would say you have a 400A Panel
Given the 400A fused disconnect before the MB Panel and no indications of a split system with 2-200A and showing 600 MCM wire and presuming CU conductors as it is not indicated, I would say you have a 400A Panel