Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
The xfrmr is feeding a MCB panel 200' away. That's it for the OCPD.Is there an OCPD on the transformer secondary at the transformer?
That sounds like a violation of 240.21(C)The xfrmr is feeding a MCB panel 200' away. That's it for the OCPD.
That's a problem. The #4 is also too small for the SSBJ.The xfrmr is feeding a MCB panel 200' away. That's it for the OCPD.
Yes, I did notice that about the neutralIf we're talking about a VE opportunity... mount the transformer close to the secondary. The 350's will need upsizing for voltage drop as well with it 210ft away. If you can't move it, you'll have to put a fused disconnect on the secondary next to the transformer.
Also, don't need a neutral conductor on your primary side.
In some brands...Probably value engineering it. 125 amp is a 200 amp frame.
Don't most discos go 30A, 60A, 100A, 200A, 400A, 600A, 800A, 1200A, etc.?In some brands...
What if this is located outside? Wouldn't 240.21(C)(4) apply?That sounds like a violation of 240.21(C)
Yes these are the break points for fuse barrel sizes.Don't most discos go 30A, 60A, 100A, 200A, 400A, 600A, 800A, 1200A, etc.?
There's nothing to indicate it's outside, but if it is, 240.21(C)(4) only applies if the feeder is outside and then into a building. In that case, you would need a disconnecting means on the outside of the building where the conduits stub in.What if this is located outside? Wouldn't 240.21(C)(4) apply?
I was responding to the frame size comment, frame sizes are in molded case circuit breakers. Some manufacturers have a 100A frame, but some are 125A, some are even 150A. Then some are 200A, or 225, or 250. From there is mostly goes to 400, 600, 800, etc.Don't most discos go 30A, 60A, 100A, 200A, 400A, 600A, 800A, 1200A, etc.?