Breaker Size

A friend of mine works in a facility where they use fusible disconnect for the transformer protection and he will always specify a 100A fuse for a 75 kVA transformer with a 480 volt primary. The 100 amp disconnect is cheaper and physically smaller than the 200 amp one that would be needed for 125 amp fuses.
 
If we're talking about a VE opportunity... mount the transformer close to the secondary. The 350's will need upsizing for voltage drop as well with it 210ft away. If you can't move it, you'll have to put a fused disconnect on the secondary next to the transformer.

Also, don't need a neutral conductor on your primary side.
 
If we're talking about a VE opportunity... mount the transformer close to the secondary. The 350's will need upsizing for voltage drop as well with it 210ft away. If you can't move it, you'll have to put a fused disconnect on the secondary next to the transformer.

Also, don't need a neutral conductor on your primary side.
Yes, I did notice that about the neutral
 
Don't most discos go 30A, 60A, 100A, 200A, 400A, 600A, 800A, 1200A, etc.?
Yes these are the break points for fuse barrel sizes.
Fuse sizes are governed by Listing, breaker sizes are more by manufacturer.

Historically commercial/industrial breaker frame sizes were 100, 225, 400, 800 and 1200A. Residential sizes of 60, 100, and 225 were common
These began to change in the 90s as AIC ratings increased, breakers became faster, and electronic trip units became more common. Today 125/150, 250, 600, and 1200 seem to be the new normal. Residential are typically 100, 150, and 250 (400 A are from the commercial world).
 
Last edited:
What if this is located outside? Wouldn't 240.21(C)(4) apply?
There's nothing to indicate it's outside, but if it is, 240.21(C)(4) only applies if the feeder is outside and then into a building. In that case, you would need a disconnecting means on the outside of the building where the conduits stub in.
 
Don't most discos go 30A, 60A, 100A, 200A, 400A, 600A, 800A, 1200A, etc.?
I was responding to the frame size comment, frame sizes are in molded case circuit breakers. Some manufacturers have a 100A frame, but some are 125A, some are even 150A. Then some are 200A, or 225, or 250. From there is mostly goes to 400, 600, 800, etc.
 