A client has an existing non-fused 100 amp disconnect for a A/C condenser that needs to be replaced. The unit calls for a max breaker size of 70 amps and min circuit ampacity of 55 amps. The conductors feeding the existing disconnect are #4 copper.
If I am interpreting the code correctly, it seems to me, that simply replacing the disconnect with an appropriately sized fused disconnect is not compliant and the breaker or conductors need to be replaced. Is this correct or is there an exception I am missing?
Somewhat adding to the complication, it seems that these particular I-line breakers are obsolete, but there should be enough room in the raceway to pull new conductors.