How do I calculate conduit fill for SER? I understand since it's one cable that it can occupy up to 53% of the conduit. Do I look at the individual conductors inside and use that in my fill calculations or the OD of the single cable and use that as my fill?
https://www.southwire.com/wire-cable/building-wire/ser-aluminum-service-entrance/p/13102901 This has an OD of .895", so to the inside diameter of my conduit would need to be 1.69" or larger to meet the 53% requirement (or 2" SCH40 PVC). Is this the correct interpretation?
https://www.southwire.com/wire-cable/building-wire/ser-aluminum-service-entrance/p/13102901 This has an OD of .895", so to the inside diameter of my conduit would need to be 1.69" or larger to meet the 53% requirement (or 2" SCH40 PVC). Is this the correct interpretation?