Fire alarm circuit 120v source separate conduit
We have always run the fire alarm circuit (120v) in new construction in separate conduit, dedicated circuit etc.. per NEC. I use to think the separate conduit was a requirement, but I have not found it in the NEC 2023. Dedicated circuit yes, conduit no. Am I missing something? Where is this found in the NEC?
What if the circuit is an emergency circuit?
I have never worked on a project where it required an emergency circuit to supply a fire alarm control panel as the panel itself is required to have battery backup power.
However, if the power source to the fire alarm control panel is supplied by an Article 700 system, then 700.10(B) would apply.
Just for the sake of being contrary, the fire alarm circuit can still share a conduit with other emergency circuits. :)
Correct. For the fire alarm systems we install the fire alarm power is always from an emergency source so it cannot be run within the same raceway as normal power. On our last project the FA power was run in Vitalink 2 hour rated cable.
New York City?
Thanks for all the responses. I think I found my answer , its more a 'local' state implied code.
WAC 296-46B-760​
Fire alarm systems.​
Device and junction boxes for fire alarm systems other than the surface raceway type, must be substantially red in color, both inside and outside. Power-limited fire protective signaling circuit conductors must be durably and plainly marked in or on junction boxes or other enclosures to indicate that it is a power-limited fire protective signaling circuit.
The red color requirement was implied also marking the conduit with red color. When we did this we didn't like other non fire alarm circuits in the same boxes and conduits since the boxes and conduits were red. ;-) This is even with normal power supplying the circuits for fire alarm.
WAC 296-46B-760​
That all appears to be talking about the actual fire alarm circuits and not about the power supply to the fire alarm control panel.
The power supply, ( or fire alarm 120v circuit that supplies the fire alarm panel) is considered to be part of the fire alarm system. This is how they have enforced it here.
This why the Circuit had to be dedicated and the breaker had to be red with a lock in the "on" position.
I don't see anything in NFPA 72 or the NEC(70) that even suggests that the power supply is a fire alarm system circuit. The red color is found in both 72 and 70, while the lock-on requirement is only in 72.
I do like your points. However, it would be hard press to convince the AHJ here in some areas that the primary power or secondary alternate power source for the fire alrm panel is not part of the "fire alarm system " seeing that the very main control panel is essential to sounding the alarm and monitoring it. And yes the power source is also monitored:🙂
Take a look at this definition from NFPA 72. The fire alarm system does not include the power supply to the control panel.
3.3.120 Fire Alarm System.
A system or portion of a combination system that consists of components and circuits arranged to monitor and annunciate the status of fire alarm or supervisory signal-initiating devices and to initiate the appropriate response to those signals.
Thanks for the info I dont have a NFPA 72. Like I said, I don't disagree with your points, but the AHJ in my area sees it differently, and I can agree with them on some level.
NEC 2023 Article 100 definitions says Fire alarm circuit: The portion of the wiring system between the load side of the overcurrent device or the powerlimited supply and the connected equipment of all circuits........
Like I stated, you would be hard pressed to convince an AHJ here that the power supply (ie fire alarm circuit) is not part of a fire alarm system. All fire alarm circuits are part of a fire alarm system. ;-)
Not sure why the NEC differs as NFPA 72 has purview for fire alarm systems.
In any case you have to go with your AHJ.
I have seen fire alarm suppression system manuals that required a private raceway for the circuit.
See NFPA 2001 (2018) at section 4.3.1.3
Initiating and releasing circuit wiring shall be installed in raceways.
Note that it doesn't say what type of raceway, so Greenfield would be acceptable.
I was referring to the power circuit. Per post #1.