JohnnyPElec
Member
- Location
- Portsmouth, VA
- Occupation
- EE
Working on a lot of commercial offices lately it would seem, with many of them having very large Open Office concepts. I keep running into Furniture systems that utilize the (2+2) electrical system, essentially meaning that 2 sets of 2 circuits, where the 2 circuits in each set share a neutral and a ground. My question is, we typically power 4-6 workstation pods with (2) 120V circuits, and have the contractor use a circuit on each of the 2 sets, simple as that. The current contractor is pushing back and saying he's only ever done it to where both circuits HAVE to share the same neutral and ground so they have to both be on the same set, but then wouldn't that mean I'd need a 2P breaker back at the source such that they have the same disconnecting means? And even if so, is there anything wrong with the approach we've been doing? I can't find where it wouldn't be code-compliant to just use one circuit off each set and be done with it
Thanks in advance!
Thanks in advance!