I'm having a circular conversation with an electrical engineer (EE) right now. Can you help me understand what I'm overlooking? This is a bare-bones commercial space, about 2,880 square feet. Our largest motor is from the HVAC unit - the compressor.
- 220.14 (C) directs us to us 430.22, 430.24 and 440.6 for load calculations
- 440.6 specifically covers air-conditioning and refrigerating equipment
- 430.1 and 440.1 seem pretty clear on the scope of what's covered by the respective article
We have sized the compressor motor OCPD at 175% of the rated load current from the face plate.
Why on earth is my EE wanting us to add another 25% for our feeder calculations? I don't see that article 430 applies to our HVAC unit.
- 220.14 (C) directs us to us 430.22, 430.24 and 440.6 for load calculations
- 440.6 specifically covers air-conditioning and refrigerating equipment
- 430.1 and 440.1 seem pretty clear on the scope of what's covered by the respective article
We have sized the compressor motor OCPD at 175% of the rated load current from the face plate.
Why on earth is my EE wanting us to add another 25% for our feeder calculations? I don't see that article 430 applies to our HVAC unit.