I've been trying to sort out when (if ever) it was acceptable to bond ground and neutral in a sub-panel in a separate building from the main service panel. Some say it's always been unacceptable since the 1923 NEC. Others give various thoughts about the NEC changing in 2008 or 1999 or sometime during/before the 1980s regarding this. It's been a bit confusing trying to sort this out.
The scenario is this:
200a main panel in a rural home (not a farm, no livestock) built in 1993. 3-wire service (2 hot, 1 neutral) then runs underground 100ft to a detached workshop. A 100a breaker in the main panel is used to run the hots which then terminate in another 100a breaker in the sub-panel. In the sub-panel the neutral is then bonded to the panel and the ground bar. This sub-panel also has a ground wire that terminates to earth. PVC was used to make the run from the home to workshop. The only other conductor connection between the two buildings is an RJ11 phone line.
I've had some people site exceptions, but suspect they're being thrown off by either the RJ11 phone line connection or the dual 100a breaker setup or perhaps local customs.
So I suppose the main questions are...
1) Was the above scenario acceptable around 1993?
2) Have bonded neutral & grounds in a detached sub-panel ever been acceptable in the NEC and if yes, what year did that change?
I appreciate any insight and education that can be shared. Thank you.
The scenario is this:
200a main panel in a rural home (not a farm, no livestock) built in 1993. 3-wire service (2 hot, 1 neutral) then runs underground 100ft to a detached workshop. A 100a breaker in the main panel is used to run the hots which then terminate in another 100a breaker in the sub-panel. In the sub-panel the neutral is then bonded to the panel and the ground bar. This sub-panel also has a ground wire that terminates to earth. PVC was used to make the run from the home to workshop. The only other conductor connection between the two buildings is an RJ11 phone line.
I've had some people site exceptions, but suspect they're being thrown off by either the RJ11 phone line connection or the dual 100a breaker setup or perhaps local customs.
So I suppose the main questions are...
1) Was the above scenario acceptable around 1993?
2) Have bonded neutral & grounds in a detached sub-panel ever been acceptable in the NEC and if yes, what year did that change?
I appreciate any insight and education that can be shared. Thank you.