Enclosure Grounding
Dale Hayes
I read a grounding specification as follows:
All grounding needs to be tied together at just one point, IE The Enclosure metal shall not be part of the equipment grounding conductor.
I can make sense of tying together at one point but I am having trouble with the following: IE The Enclosure metal shall not be part of the equipment grounding conductor.
What is this specification a part of?
Metal enclosures for electrical equipment must be grounded and bonded. This by default will make the enclosures part of the equipment grounding conductor.
Chris
Short Answer......
They want you to install an EGC of the wire type. (side note- But do not isolate electrical equipment that is likely to become energized....make sure it is all bonded together. )
I would agree with Daniel. Sounds like spects that require ground bars and equipmet grouning conductors (wires) throughout the system.
Not a Code requirement.
If that is indeed the intent of the spec, then the way the spec is worded it is very poor at best.
Chris
Chris
Agreed.......I have encountered similar specs, sometimes having to educate the "powers that be" of the dangers involved and code requirement . Don't take it for granted that an Engineer is going to understand the intent of the NEC, and/or follow it for that matter(typically they have the most influence in 16000).
Thery are just trying to say it needs to be a seperate EGC.