4 wire dryer Recept.

Status
Not open for further replies.

Raccoon 3

Member
Where in code book does it state the requirement for 4 wire cord and Recept use for dryers and Ranges in single family dwellings.
 
try 250.142 (B) Load-Side Equipment. Except as permitted in 250.30(A)(1) and 250.32(B), a grounded circuit conductor shall not be used for grounding non?current-carrying metal parts of equipment on the load side of the service disconnecting means


be sure to read exceptions
 